concrete thickness and psi for a honey house
Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2011
    Location
    Winter Garden, Fl
    Posts
    45

    Default concrete thickness and psi for a honey house

    plz help me with the recommended concrete thickness and psi for a honey house

    thanks

  2. Remove Advertisements
    BeeSource.com
    Advertisements
     

  3. #2
    Join Date
    Mar 2014
    Location
    Walton County, GA
    Posts
    144

    Default Re: concrete thickness and psi for a honey house

    A 4" slab of standard 3,000 psi concrete thickened at load-bearing walls (or with concrete piers for columns / posts) should be sufficient. Of course, a thicker slab may be needed where a heavy piece of equipment or heavy stored items are located. Be sure the soil where you plan to pour the slab is properly compacted before pouring concrete.

    Is a building permit required in your area? If so, you will need to specify things like concrete slab thickness and minimum strength before getting a permit.

  4. #3
    Join Date
    Jan 2012
    Location
    D/FW, TX
    Posts
    124

    Default Re: concrete thickness and psi for a honey house

    We did a 6" with a lot of rebar in case we wanted to use the skid steer inside, which we have had to do. We had to pull our honey sump out of the floor to replace the heating element. It was nice not to worry about the floor.

  5. #4
    Join Date
    Jun 2007
    Location
    mineral county,Montana USA
    Posts
    1,325

    Default Re: concrete thickness and psi for a honey house

    i poured mine 6", 5 1/2 sack mix. i put in 3 zones of radiant heat, sloped the floor to my drains, and hired people better than me to finish it. Just got the outdoor wood boiler hooked up to the floor last week. happy with everything so far.

  6. #5
    Join Date
    Feb 2006
    Location
    Herrick, SD USA
    Posts
    6,573

    Default Re: concrete thickness and psi for a honey house

    Yes, if you are planning on forklifts or trucks being driven on it, 6" with plenty of rebar is what you want. Do concrete right or you will always regret it.
    "People will generally accept facts as truth only if the facts agree with what they already believe."- Andy Rooney

  7. #6
    Join Date
    Jul 2011
    Location
    Winter Garden, Fl
    Posts
    45

    Default Re: concrete thickness and psi for a honey house

    Jim, how about PSI?

  8. #7
    Join Date
    Apr 2014
    Location
    Powhatan, Virginia, USA
    Posts
    356

    Default Re: concrete thickness and psi for a honey house

    Psi is not as critical, 3000 should be fine unless you are point loading something heavy on a very small footprint. Proper compacted base, so the slab is evenly supported, rebar and wire to spread the load, and proper thickness especially if using the edges as footings are the most important. Good finishing to consolidate the surface is also important, and don't rush to use it until it can cure. 75% strength in 7 days, most at 28 days, unless you pay more for high early strength mix.

  9. #8
    Join Date
    Jul 2011
    Location
    Winter Garden, Fl
    Posts
    45

    Default Re: concrete thickness and psi for a honey house

    thanks.

  10. #9
    Join Date
    Mar 2010
    Location
    Santa Fe, NM
    Posts
    1,222

    Default Re: concrete thickness and psi for a honey house

    This post reminds me of what my old boss used to say many years ago when I worked construction.."ya know there are two kinds of concrete...concrete that's cracked, and concrete that's gonna crack".. get a compaction test as the soil prep is very important. Even on all sand like in Florida..